A commercial refrigerator with refrigerant-134a as the working fluid is used to keep the refrigerated space at −30°C by rejecting its waste heat to cooling water that enters the condenser at 18°C at a rate of 0.25 kg/s and leaves at 26°C. The refrigerant enters the condenser at 1.2 MPa and 65°C and leaves at 42°C. The inlet state of the compressor is 60 kPa and −34°C and the compressor is estimated to gain a net heat of 450 W from the surroundings. Determine (a) the quality of the refrigerant at the evaporator inlet, (b) the refrigeration load, (c) the COP of the refrigerator

Respuesta :

Answer:

A) The quality of the refrigerant at the evaporator inlet = 0.48

B) The refrigeration load = 5.39 kW

C) COP = 2.14

Explanation:

A) From the refrigerant R-144 table I attached,

At P=60kpa and interpolating at - 34°C,we obtain enthalpy;

h1 = 230.03 Kj/kg

Also at P= 1.2MPa which is 1200kpa and interpolating at 65°C,we obtain enthalpy ;

h2 = 295.16 Kj/Kg

Also at P= 1.2MPa which is 1200kpa and interpolating at 42°C,we obtain enthalpy ;

h3 = 111.23 Kj/Kg

h4 is equal to h3 and thus h4 = 111.23 Kj/kg

We want to find the refrigerant quality at the evaporation inlet which is state 4 and P= 60 Kpa.

Thus, from the table attached, we see that hf = 3.84 at that pressure and hg = 227.8

Now, to find the quality of the refrigerant, we'll use the formula,

x4 = (h4 - hg) /(hf - hg)

Where x4 is the quality of the refrigerant. Thus;

x4 = (111.23 - 3.84)/(227.8 - 3.84) = 0.48

B) The mass flow rate of the refrigerant can be determined by applying a 1st law energy balance across the

condenser. Thus, the water properties can be obtained by using a saturated liquid at the given temperatures;

So using the first table in the image i attached; interpolating at 18°C; hw1 = hf = 75.54 kJ/kg

Also interpolating at 26°C; hw2 = hf = 109.01 kJ/kg

Now;

(mr) (h2 − h3)= (mw) (hw2 − hw1)

mr is mass flow rate

Making mr the subject, we get;

mr = [(mw) (hw2 − hw1)] /(h2 − h3)

mr = [(0.25 kg/s)(109.01 − 75.54) kJ/kg

] /(295.13 − 111.37) kJ/kg

mr = 8.3675/183.76

mr = 0.0455 kg/s

Formula for refrigeration load is;

QL = mr(h1 − h4)

Thus,

QL = (0.0455 kg/s)(230.03 − 111.37) kJ/kg = 5.39 kW

C) The formula for specific work into the compressor is;

W(in) = [(h2 − h1)] − (Q(in

)/mr)

= (295.13 − 230.03) kJ/kg − (0.450kJ/s

/0.0455 kg/s)

= 65.10 Kj/kg - 9.89 Kj/kg

55.21 kJ/kg

Formula for COP is;

COP = qL

/W(in)

Thus; COP = (h1 − h4)/W(in

)

= [(230.03 − 111.37) kJ/kg

] /55.24 kJ/kg

= 2.14