Purely resistive loads of 24kW, 18kW and 12kW are connected between the neutral and the red, yellow and the blue respectively of 3 phase, four-wire system. The line voltage is 415. What is the current in each line conductor ?

Respuesta :

Lanuel

Answer:

The phase current in each line conductor are;

[tex]I_{R} = 100.17 < 0A[/tex]

[tex]I_{Y} = 75.13< - 120A[/tex]

[tex]I_{B} = 50.08 <120A[/tex]

Explanation:

Given the following data;

Red phase = 24kW,

Yellow phase = 18kW

Blue phase = 12kW

Line voltage = 415V

For a star connected system, we have;

[tex]Phase voltage (V_{p} ) = \frac{Line voltage}{\sqrt{3}}[/tex]

[tex]Phase voltage (V_{p} ) = \frac{415}{\sqrt{3}}[/tex]

[tex]Phase voltage (V_{p} ) = 239.6V[/tex]

The phase sequence for RYB is given by;

[tex]V_{R} = 239.6<0\\V_{Y} = 239.6<120\\V_{B} = 239.6<-120[/tex]

[tex]Phase current (I) = \frac{Phase power}{Phase voltage}[/tex]

[tex]Hence, I = \frac{P}{V}[/tex]

For the Red phase;

[tex]I_{R} = \frac{24000}{239.6<0}[/tex]

[tex]I_{R} = 100.17 < 0A[/tex]

For the Yellow phase;

[tex]I_{Y} = \frac{18000}{239.6<120}[/tex]

[tex]I_{Y} = 75.13< - 120A[/tex]

For the Blue phase;

[tex]I_{B} = \frac{12000}{239.6<-120}[/tex]

[tex]I_{B} = 50.08 <120A[/tex]

For the line neutral;

[tex]I_{N} =\sqrt{ (I_{R}^{2} +I_{Y}^{2}+I_{B}^{2}-I_{R}I_{Y}-I_{Y}I_{B}-I_{R}I_{B}[/tex]